[#1]
@ZW17:
Thanks for all your knowledge. I have a Trane XV95 furnace and XL16i heat pump, both installed in 2010. Regular maintenance every six months, but no A/C as of yesterday. Tech came out and said reverse valve leaked, compressor ran without refrigerant. Reverse valve cannot be fixed, must be replaced, because in a bad spot. Safety valve also needs to be replaced because it failed. Condenser fan also failed. Several thousand dollars to fix. Tech also wanted us to consider whole new system. 3 options Amana heat pumps ASZ160601, ASZC160601, or ASZC180601 with furnaces AMEX or AMVC. Obviously quite expensive. I'm getting a second opinion from a Lennox dealer tomorrow. 1) Are these Amana units any good? 2) Is 14 years a reasonable lifespan? 3) Does the tech explanation for the failure make sense? Thanks! |
|
|
[Last Edit: shooter_tx]
[#2]
Originally Posted By ZW17:I’d always get a minimum of three quotes, maybe even a 4th or 5th if it was a complicated project. View Quote I've got my first quote. In getting my next 2-5, I've noticed some big-box type folks (Home Depot, Lowes, Costco, and maybe Sam's?) are also in the game. Obviously they're not going to be doing the work themselves (lol), but are there any reasons to either include or avoid these folks? (for either their estimates, or the actual work) I was specifically thinking about that Costco warranty... which I don't even know if it'd apply to 'their' HVAC work, but I thought it was at least worth asking about. |
|
|
[#3]
Originally Posted By shooter_tx: I've got my first quote. In getting my next 2-5, I've noticed some big-box type folks (Home Depot, Lowes, Costco, and maybe Sam's?) are also in the game. Obviously they're not going to be doing the work themselves (lol), but are there any reasons to either include or avoid these folks? (for either their estimates, or the actual work) I was specifically thinking about that Costco warranty... which I don't even know if it'd apply to 'their' HVAC work, but I thought it was at least worth asking about. View Quote Do NOT use the box store contractors for ANYTHING, EVER, including flooring, tile, etc.... They are one step above home warranty contractors in terms of quality. Pure garbage. |
|
Why do you own a fire extinguisher when you have the fire department to protect you?
Politicians should wear uniforms like NASCAR drivers so we could see their corporate sponsors. |
[#4]
Originally Posted By YGBSM: @ZW17: Thanks for all your knowledge. I have a Trane XV95 furnace and XL16i heat pump, both installed in 2010. Regular maintenance every six months, but no A/C as of yesterday. Tech came out and said reverse valve leaked, compressor ran without refrigerant. Reverse valve cannot be fixed, must be replaced, because in a bad spot. Safety valve also needs to be replaced because it failed. Condenser fan also failed. Several thousand dollars to fix. Tech also wanted us to consider whole new system. 3 options Amana heat pumps ASZ160601, ASZC160601, or ASZC180601 with furnaces AMEX or AMVC. Obviously quite expensive. I'm getting a second opinion from a Lennox dealer tomorrow. 1) Are these Amana units any good? 2) Is 14 years a reasonable lifespan? 3) Does the tech explanation for the failure make sense? Thanks! View Quote Sorry I missed your post. Hopefully this gets to you in time. Yes, everything your tech said makes sense. 20yrs is a good lifespan for HVAC. Amana is a solid mid grade unit. I would install one in my home. Good warranties. |
|
Why do you own a fire extinguisher when you have the fire department to protect you?
Politicians should wear uniforms like NASCAR drivers so we could see their corporate sponsors. |
[#5]
Dang, this thread has just turned 10yrs old.
|
|
Why do you own a fire extinguisher when you have the fire department to protect you?
Politicians should wear uniforms like NASCAR drivers so we could see their corporate sponsors. |
[#6]
And I still subscribe to it.
|
|
|
[#7]
|
|
Fetchez la vache!
|
[Last Edit: Defender3]
[#8]
Thanks for keeping a great thread going for 10 years! Hope this is the right place to ask a question.
Wife noted the AC was not working. I checked the Sensi thermo and there was no power to the unit that (obviously) comes from the furnace controller. I checked and reset the breaker, then the power to the unit, then checked the LED, which was blinking steady, supposedly an error indicating no call for heat. Reset the error code counter and and the power again and it is still blinking. Replaced the 5a fuse, still the same. Unit is a 5-year old Trane XR95 with a natural gas furnace and apparently has no power past the board. No way (for me) to test the transformer (could it be that easy??). No idea why a call for heat would lock out or cause the issue (heat has been off for a while here in VA). Getting ready to call the pros, is there anything I should smarten up on so they don't roll me? TIA. |
|
President, Quantico Shooting Club
Back the Blue |
[#9]
Not much else to say except let the pros do their work and track down what has failed.
I have never had many issues with Trane’s boards. I hope it’s something easy and not too expensive. The on call guy is not looking forward to his 4pm Friday call. |
|
Why do you own a fire extinguisher when you have the fire department to protect you?
Politicians should wear uniforms like NASCAR drivers so we could see their corporate sponsors. |
[#10]
Originally Posted By ZW17: Not much else to say except let the pros do their work and track down what has failed. I have never had many issues with Trane’s boards. I hope it’s something easy and not too expensive. The on call guy is not looking forward to his 4pm Friday call. View Quote Appreciate the quick reply! It's only in the high 70s here today so I gave the on call tech a break and scheduled for tomorrow morning. :) Seriously though, any scam they can run on me like the flux capacitor is bad???? |
|
President, Quantico Shooting Club
Back the Blue |
[#11]
Originally Posted By Defender3: Appreciate the quick reply! It's only in the high 70s here today so I gave the on call tech a break and scheduled for tomorrow morning. :) Seriously though, any scam they can run on me like the flux capacitor is bad???? View Quote There is always the risk, and there is little you can do to limit your exposure to those guys. Trust your gut and ask the guy to leave if the alarm bells are ringing. |
|
Why do you own a fire extinguisher when you have the fire department to protect you?
Politicians should wear uniforms like NASCAR drivers so we could see their corporate sponsors. |
[#12]
Do you hear the connector on the board snap shut to send power to the blower?
|
|
"The credit belongs to the man who is actually in the boogaloo, whose face is marred by pixels and ink and cheetos.”,
Teddy the Toad, (w,stte), "The Derpmen" |
[#13]
|
|
President, Quantico Shooting Club
Back the Blue |
[#14]
You can bypass a contactor with stout wire as a test
|
|
"The credit belongs to the man who is actually in the boogaloo, whose face is marred by pixels and ink and cheetos.”,
Teddy the Toad, (w,stte), "The Derpmen" |
[Last Edit: Defender3]
[#15]
Originally Posted By doc_Zox: You can bypass a contactor with stout wire as a test View Quote The tech is scheduled between 8-12am today so let's see what they say. Unit was also installed exactly 5-years ago, so fingers crossed there may be an actually useful warranty. ETA - OP is about a dumba$$. Unit has two drains and OP only checked one. Tech opened it up and sure enough it was backed up and triggered some electronic float. Thumped the drain pipe and the universe was restored to balance. Geeeezus I feel stupid right now..... Thanks to all who chimed in. And I did jump R to G and the blower worked, then R to Y and the blower and compressor worked. Just didn't think to pop that other cap off and check the drain... |
|
President, Quantico Shooting Club
Back the Blue |
[#16]
One winter I had the webbing that supported my vent pvc 15 foot pipe run fail and the horizontal pipe slumped towards the furnace
Pipe condensant drained toward the gas furnace rather than away, and the fitting at the unit dropped below plumb and did not drain same blinking light and no blower blowing out the drain lines every season is a good plan |
|
"The credit belongs to the man who is actually in the boogaloo, whose face is marred by pixels and ink and cheetos.”,
Teddy the Toad, (w,stte), "The Derpmen" |
[#17]
Originally Posted By doc_Zox: One winter I had the webbing that supported my vent pvc 15 foot pipe run fail and the horizontal pipe slumped towards the furnace Pipe condensant drained toward the gas furnace rather than away, and the fitting at the unit dropped below plumb and did not drain same blinking light and no blower blowing out the drain lines every season is a good plan View Quote I assure you it will be on my maintenance plan going forward. |
|
President, Quantico Shooting Club
Back the Blue |
[#19]
Any opinion on the York brand?
|
|
|
[#20]
Originally Posted By TexasDoubleTap: I have one for the math nerds and HVAC enthusiasts. How do I calculate the CFM flow potential of a goofy flush mount grill like pictured below. Have a guy who wants to go from a 4 ton up to a 5 ton variable speed. He can certainly use the extra capacity during the dog days of summer. https://www.ar15.com/media/mediaFiles/214369/DrywallAir_1_13ddd6fb-346e-4ca0-b6a7-962-2868264.jpg Great thread. I'm in the biz and still learn from reading here and in other hvac posts. Always something new to learn in this biz. The one I'm calculating for is: 20.5" wide overall 32.5" tall overall Channel is 1.75" wide on all sides View Quote 20.5 x 1.75 x 2 = 71.75 sq/in 32.5 x 1.75 x 2 = 113.75 sq/in Round this up for easier math 72 + 114 = 186 sq/in for air to flow through that funky grille. Same as a 10x18 duct = 180sq/in. Now let’s put that on a ductulator and see what you flow at .5” of static pressure which most residential systems are designed around (max). 3” is more better though. 10x18 duct at .3” of SP is pushing 2000cfm. 400cfm per ton = 5 tons. One outlier is how long of a ducting run from the furnace to the grille? FYI: Ducting design and air balance is not my strong point, please have this checked before doing that install. Lots of ductulator apps for phones out there. |
|
Why do you own a fire extinguisher when you have the fire department to protect you?
Politicians should wear uniforms like NASCAR drivers so we could see their corporate sponsors. |
[#21]
|
|
Why do you own a fire extinguisher when you have the fire department to protect you?
Politicians should wear uniforms like NASCAR drivers so we could see their corporate sponsors. |
[Last Edit: DeltaAir423]
[#22]
Awesome thread, I subscribed after I had my system redesigned and replaced. But I still am catching up.
BTW, I went from a Goodman 3 ton 13 SEER heat pump covering 2800 sq ft living area and a Goodman 1.5 ton 13 SEER heat pump with a 1 ton air handler covering 300 sq ft, to a single Carrier 4 ton 26 SEER heat pump variable speed compressor and air handler with zoned dampeners. For the first month I had the new system, I was always going out and checking the compressor, because I can't hear it. |
|
Arthur Dent: ALLRIGHT, WHERE IS SHE?!?!?
Vogon Receptionist: Who, the director of robot arm repair? Xbox Live GT: DeltaPlaneMech PSN ID: DeltaAir423 MoS# 42 |
[#23]
So here's a .. we'll call it a challenge.
I've got a 2000sq/ft shop that I need to install AC in. I've been using a 4 Ton water source heat pump up to this point that I made portable. It's been handy, I've loaded it up on a trailer and taken it to a friends house to work in his shop in comfort. but I digress. The down side is my well runs along with the heat pump which adds to the energy cost & the unit is probably 30 years old at least. A friend recently replaced his 13 SEER 5 Ton Trane HVAC because the evaporator rusted and developed a leak. Trane wanted an insane amount of money for a new coil + labor so he elected to upgrade to a new variable speed unit. I took advantage of the opportunity and asked him to same his old system for me. I had him have the tech reverse pump the Freon R410, back into the compressor to save it. It's a Heritage 13 condenser unit mfg in 2009. (I have all the model#'s if needed) I've been researching cased coils (& uncased), & AHU's Lots of freight damaged & discontinued NOS stuff out there that's pretty cheap. The dead AHU has a TXV. I've been shopping for 5 Ton evaporators with TXV, R410, 24x21 cabinet. Is there anything else I should be looking at to ensure compatibility with the condenser? Anything to avoid at all costs? I have access to a Scorpion 2000 recovery vac unit, gages, clamp on amp meter, oxy torch other tools. I have argon that I can purge with. Admittedly I've never done home HVAC but I've done plenty of automotive in the past. I'd only have the cost of the coil in it and if I got 5-10 years from it, it would be worth it in the end. Any sage advice? |
|
How come every time there is a shooting, they want to take away the guns from the people who didn't do it?
|
[#24]
What are the thoughts of mini splits vs heat pump vs heat pump/gas (dual fuel) if the entire system will be built from the ground up?
I'm in the process of trying to get something done to my place right now. It has a rigged in poorly done central gas furnace in a tight crawlspace, but never had central heat. Been getting quotes on having a new system installed in either a closet or the attic with ducting in the attic. Electrical will need to be run as well. |
|
|
[#25]
Oversized equipment will not control the humidity. The unit only dehumidifies while it's running, so if your on the boundary, get the smaller unit.
|
|
Another old guy
|
[#26]
I'd suggest that you have your oil burner serviced annually. Burner nozzles wear fairly quickly, fuel pumps can lose pressure, something went out of adjustment and it sooted up internally. It should take 1 to 2 hours for a proper clean and tune up..
|
|
Another old guy
|
[#27]
Hoping this is the right place to get an opinion on brands/course of action.
Have a 1050 sq foot side of a duplex that had trouble cooling this year in central texas (we all did at 108 for a few weeks). System got weaker and weaker. I put gauges on it and had 3 techs out from diff companies to verify it's low on freon, the evap in the attic is most likely the problem and to discuss replacement options. This is a R-22 system from install with the home being built in 2001. Compressor sounds noisy, but i'm thinking that's due to being low on freon. Issue at hand- Do I repair it myself or update to a new system. On the other side of the duplex 2 years prior, I had the same issue. System completely leaked down due to leak at the evap. I ordered a new one off the net, installed and vacuumed down. Had a tech out who had some R-22 to fill it back up and it's been working ever since. Today i've found a replacement evap for the broken side, but am having trouble finding a tech who will buy R-22 or the synthetic stuff. Since both sides are R-22, I've offered to pay for the whole can and keep it in the event the other side has issues. Tech 1 uses solely Trane. I can't get them to call me back now, but haven't put much effort into it except an initial phone call. Tech 2 uses goodman but doesn't install himself. He farms it out to another co so that tells me he's out of consideration. Tech 3 is suggesting a Nortek Gas 15 seer @ $7,500 or a Ducane dual fuel 16 seer @ $7,900. I've never heard of these brands. Google searches bring up all sorts of differing answers. The pitch is - "Norteck makes maytag, frigidaire and gibson. All brands i've never new were involved in home AC except gibson. The Ducane is an advanced series by Lennox. They carry Trane OXbox but it has bad metering devices and is a low budget unit. Carrier is known for coil leaks. Trane has poor tech supports and warranty issues but Trane and Carrier have good commercial unites. Goodman, Daikin, Trane, CArrier, Bryan, Payne all use the same basic coil design. A ribbon candy coil that causes the compressor to run at higher thermal temp vs system they support that uses a backward Z design that maintains a lower temp due to less heat restriction preventing thermal lock overload. They also come with storm damage protection from hail." Does that sound correct to anyone with more experience than I? If it was a vehicle, I could tell you individual vehicles and models to avoid by year. I can't do that with AC systems and it's making me nervous picking such an expensive product. |
|
|
[#28]
FWIW of the 80+ brands in the American market there are only 7 manufactures. Nortek uses industry standard copeland compressors, galvanized powder coated sheet metal, composite pans and all aluminum coils. The Maytag label has one of the best warranties in the business at 12 years. Whatever brand you go with, it will depend on the quality of the install as to how it performs. I have a five stage Maytag HP that has been in for four trouble free years.
|
|
Matthew 5:9 Blessed are the peacemakers,
for they will be called children of God. |
[#29]
that is what i am seeing in my research as well. The only hold up i'm having is in comparison to say autos. I think my local tech or forum is the best for say the ford brand. That still doesn't get me around the issue that some of their products are just duds like the 6.4 diesel no matter how good the tech is. Was hoping to see if these installers sounded legit and if any of these brands/models were in the total avoidance column.
|
|
|
[#30]
How are the Pioneer ducted split units? (Not "mini-split") The bigger 3.5 0r 4 ton split systems with and air handler, and the outside unit that has the fans on the side instead of on top.
|
|
|
[#31]
|
|
What is a democrat? Someone who wants everything you have, except for your job.
Politicians should wear uniforms like NASCAR drivers so we could see their corporate sponsors. |
[#32]
Is there a WiFi thermostat you recommend?
One where I can access it with my phone, but not give the app/thermostat any more data than necessary? |
|
|
[#33]
Originally Posted By Maverick17: Is there a WiFi thermostat you recommend? One where I can access it with my phone, but not give the app/thermostat any more data than necessary? View Quote https://www.honeywellhome.com/us/en/products/air/thermostats/wifi-thermostats/wifi-9000-color-touchscreen-thermostat-th9320wf5003-u/ Stay away from the Google Nest. From my understanding, that thing is a spy machine in your house. I’m sure the Honeywell is also gathering and selling data, but I just don’t know about it. |
|
What is a democrat? Someone who wants everything you have, except for your job.
Politicians should wear uniforms like NASCAR drivers so we could see their corporate sponsors. |
[#34]
Thanks,
Honeywells site says I need a professional to install. That’s just a suggestion right? I’ve replaced a thermostat before, this isn’t anything more complex on the install side from what my non hvac brain can see? |
|
|
[Last Edit: ZW17]
[#35]
Originally Posted By Maverick17: Thanks, Honeywells site says I need a professional to install. That’s just a suggestion right? I’ve replaced a thermostat before, this isn’t anything more complex on the install side from what my non hvac brain can see? View Quote Turn power off at the furnace or air handler. Wire for wire, mount on the wall, program. Power back on. Test operation. |
|
What is a democrat? Someone who wants everything you have, except for your job.
Politicians should wear uniforms like NASCAR drivers so we could see their corporate sponsors. |
[#36]
Thanks
|
|
|
[Last Edit: AJ_Dual]
[#37]
@ZW17
Apologies in advance for the "War & Peace" tl/dr story here... I have a significant: "I'm poor/broke, with a bunch of ad-on 'There's a hole in the bucket dear Liza' stuff,"-AC problem. And I feel as if my options are to do something janky & DIY I can afford, or do nothing, and limp indefinitely on window box AC's, which, I need anyway, more on that below. I have a 1929 Milwaukee 'burbs craftsman 2-story bungalow. Roughly 1800 sqft. With 3/4's of the basement finished. I and my wife bought it in 2000. It came with a 1997 vintage Bryant nat. gas non-efficient forced air furnace. And it has an R-22 A-frame upflow evaporator with 2.5 (you may already see an issue...) ton capacity. And a Bryant brand condenser outside in the back yard. On the heat side, I've gotten very very good at troubleshooting all the various proof-of-flame thermocouple, vacuum airflow diaphragm switch, fusable link overtemp cutoff, ignitor glow plug aging, & insufficient voltage & resistance, the whole damn mainboard, and motor stater capacitors. In 2010, in the middle of a hot summer, with four young daughters, back-to-back twins, 11 months apart, the AC died. And Mrs. Dual & I needed that fixed ASAP. I already knew enough to troubleshoot decently, and followed the issue to the condenser. Corrosion & dirt allowed the start capacitor to arc into the main compressor capsule when it attempted to start, and besides the short preventing startup, it actually melted a hole into the compressor pod, and all the R22 had vented. We called a local well regarded HVAC company, and the estimator/service writer was a good guy, and explained what was coming up with the stages of the R-22 ban, and what our options were. And he understood our need for a minimum effort & minimum cost repair. So they did a dry-nitrogen filled generic OEM condenser, keeping the original '97 Bryant A-frame evaporator, because some of it had to stay to make it a legal "repair" to use R22 for a recharge. So they sweated the OEM dry N2 condenser on, and recharged it. All for $3500. Parts & labor. Which I believe was an average & okay price. And I appreciated them understanding we could only afford the minimum, not being pushy or upselling, plus the R22 grandfather repair issues. Now, in 2024, I'm a widower, down to one income, with four girls in college. And I ain't got the $3500, even if that sum would fix my AC, which it won't. This year, the condensate drain was plugged up inside the drip pan under the evaporator. I was careful as possible to not move anything other than the sheet metal to gain access. I scraped/flushed out all the moldy Legionaire's Disease snot, and since I was in there, I sprayed down the coil with no-touch coil foam cleaner. I did have to move the coil a little, just an inch or two, letting the big copper cold side supply and little copper hot side return do the bending, ensuring they didn't kink. Did I just whiff something minty + magic marker smelling? Ohhhh shiiit. Smell again, repeatedly, nothing. Shut off every noise in the house possible, listen, nothing. The foam cleaner & rinsing was a decent soap bubble check too. Nothing... (At least on the sides of the evap. I could see without risking even more big movements) Okay, I'm just paranoid... probably. Close it up, throw the breaker for the condenser, turn HVAC stack power on, make sure the WiFi thermostat is calling for AC... It starts up, blows cold air, and the condensate tube is draining nicely. Next morning, AC is blowing, but it's not cold. Micro cracks or pinholes in the evaporator, dissimilar metals corrosion between the copper, aluminum, steel, lead/tin soldering, and the coil was nearly 30 years old. I get it. But, being broke-ass widower me, I can probably only swing the price of parts... if I can make it work. That would be keeping the newer 14 y.o. condenser, as I've neuroticaly kept it covered in winter, and clean, like Cameron's Dad's Ferrari in "Farris Bueler's Day off" after what happened to the first one. So sweat on a new R-22 & "compatible multi-refrigerant" upflow 2.5 ton A-frame, and charge it with R-442D/MO59, assuming I can find a small non-rape priced 5 lb. bottle just for me, as I don't need 20 lbs. to service a few houses. And assuming there's not a MO oil vs. R-442D vs. POE oil problem, that means I can't do any of that. The house came with only a 2.5 ton AC because everything the previous owners did, and what little they paid anybody that was a pro in the relavant trades to do... was bare-minimum cheap, DIY, & shitty "Mad Max Master-Blaster runs Bartertown!" or maybe, "Gilligan's Island bamboo & coconuts style" remodeling & upgrading. Siding, roof, gutters, windows, doors, trim, insulation, electrical, plumbing... I could write a post as long as this about each of these. And that includes the forced air ducts. No balancing whatsoever, nonsense cold air returns, or none. And they were merely proud they figured out a way to get a duct to each room with as little upset to walls or carpentry as they could. Too many 90° bends, shape & size changes, or, no duct at all. Just using the void between two studs and the plaster, lath, or drywall as a riser. All stuff I had no clue about when I was 26 years old back in 2000. Nor did I know that many "home inspectors"... most just collect a check to sign off on bank & insurance paperwork, and only look for obvious things that'll break in under a year, or might kill the homeowners with CO asphyxiation and get them sued. So there's no point in upgrading the whole HVAC stack, unless I can also afford a bunch of demolition & repairs so properly done ductwork can go in. Or, maybe they demo my old brick coal/oil furnace chimney the furnace & gas water heater use still use. And the void from removing it, could be ysed to run those narrow high-velocity air flexi ducts. If they're even a thing, or still "in fashion." |
|
Like most Americans, I learned all I needed to know about the Vietnam War by watching M*A*S*H*...
|
[#38]
@AJ_Dual
I read you book, you have a way with words, it was funny. But is there a question in there that I can answer? If you are asking what to do... If the ducting has been working for 20+ years with 75k BTU's (guessing, you didn't say) of heat and 2.5t of cooling. I say replace the minimum of the furnace and AC. I mean you need it, you really can't get away without it, and you're not paying to reinvent the wheel. Mini splits are an option, but you will need new electric run all over the house to support multiple systems, or big power run to the condenser and refrigerant lines run through the home to the evaporators. I think your most economical route would be to swap out the existing gas furnace and AC. Thoughts? |
|
What is a democrat? Someone who wants everything you have, except for your job.
Politicians should wear uniforms like NASCAR drivers so we could see their corporate sponsors. |
[Last Edit: AJ_Dual]
[#39]
@ZW17
Thanks for replying! And again, I'd so gladly pay to have this done. It's simply a matter of its DIY this at parts-cost, or do nothing, essentially. And your reward is... shit. Another novel. I agree that the most economical approach is replacing the minimum of the HVAC too. And yes, the AC pushing cold air up against gravity, with bad slow ducts and an inadequate 2.5T AC sucks, but "just live with it" is okay. Especially since at least heat passively rising in winter more or less works out okay, leaving none of the 2nd floor rooms freezing. And on this plan, the furnace stays. It works, and except the one time in 2014 the main board died, it's all been common replacement parts, sensors, and the main blower start capacitor... So my concise, pointed question is... My idea of spending about $800-1000, for: 1. An R-22 & "compatibles" 2.5T A-frame upflow evaporator that fits, same dimensions as the old one. 2. Keeping my existing R22 condenser outside. 3. Getting a $100-ish Amazon or Harbor Freight hi/lo manifold testing & recharge/fill gauge & hose set. 4. A small 5lb bottle of R-224D/MO59... Is that possible? Any immediate problems or incompatibility? Additional questions: - Is there a problem with the R22 condenser if it has mineral oil in it, if I fill with R-224D that has POE/synthetic mixed in the bottle? (I assume it's just in the refrigerant, right? And it sprays or carries in with a fill or recharge? Seems like an assumed thing "you are supposedto already know.") - If existing MO in the compressor, coils & lines IS definitely "a no-no," either because it shouldn't be mixed with POE, or the R-224D, or both (Everybody's explanation on this all differ, and it is unclear. There's no nice OK & NOK matrix grid of combinations covering all combinations.) - Is there a definite way to confirm if my existing R22 dry N2 replacement compressor has MO or POE in it? From a tech datum on its labels? Some other way? - If this is all OK and in theory is compatible and "should work" (not counting if I actually screw up doing it somehow, of course) are there pitfalls and scams I should be aware of? Vendors to avoid, vendors to trust? Anything about trying to buy a bottle of R-224D I should be aware of? - Just Googling possible items, and seeing the search results, sets off my spider sense. Even though I am searching on R-224D/MO59, there's tons of listings for R-22 at very good prices. Like WTF is this below? I assume it's a China based website, so are they just doing the: "IDGAF, ship it, see if it makes it through CBP to the US buyer?"-thing? AFAIK, it's supposed to be illegal/phased out worldwide, with only narrow exceptions? But...China is probably DGAF on that too, and the grandfathered supply, or very limited "nothing else works" exceptions, they just wholesale abuse that?" So, even if my minimum parts, zero labor idea is technically feasible, I worry there's another whole layer of fly by night scamming. And the top selling hits for things like: "Upflow A-frame R22 2.5 ton 18"x17"x20" turn up this: https://www.acwholesalers.com/Goodman-CAUFA2922B6/p114284.htmldXxoCvDMQAvD_BwE This is a fly-by-night borderline scamming place? I'm not even saying it's exactly the right evaporator... just an example. But I have a hunch, and it all makes me think there's a large scammer or legal-but-shady Industry aimed at fleecing guys that are either stungy/cheap, or desperate & broke (me) and have "some idea of what they're doing" but aren't full-time HVAC guys in the know. Or, it's a drop-shipping front, trying to refer you for installation through a HVAC service network with kickback comissions. |
|
Like most Americans, I learned all I needed to know about the Vietnam War by watching M*A*S*H*...
|
[#40]
You are not supposed to mix oils, it's not the end of the world if you get some containments in there, but I wouldn't be putting an entire compressors worth of oil in a system. Gelling was the major concern, and once that happens, you are in a world of trouble to try and clean that up.
Dry ship (nitrogen filled) is still out there but very hard to find. If you can locate it, it should be fine. I cannot recommend one brand over another, I honestly haven't bought any dry ship equipment in years. R22 has been dead in the commercial/industrial side for years. Our customers equipment has sometimes hundreds of pounds of refrigerant, they changed over to R410, R407, and R134 years ago. I would recommend replacing both the evap and condenser, it's a few hundred more for the condenser with the cheaper lines of equipment. No sense in hacking the system up to save $400, but I don't know your financial situation. Harbor Freight stuff will get you through a job or two, it's really your only option unless you have somewhere that rents near you? To recap: - Don't mix oils, not a good practice. - Recommend spending the money to move away from R22 everything and bite the bullet and go to newer refrigerants. - Harbor Freight will get you by in a pinch. - Don't buy the overseas R22, it's both illegal for you to ship and it's quality would be questionable. - Every manufacturer has off brands (Carrier is Bryant, is Payne). Go with a lesser brand like Payne and save hundreds for basically the same equipment. Sorry, in an end of the week rush at work, I wish I had more time to give a more thorough answer. |
|
What is a democrat? Someone who wants everything you have, except for your job.
Politicians should wear uniforms like NASCAR drivers so we could see their corporate sponsors. |
[#41]
ACWholesalers.com is GTG. I purchased a 4 ton gaspack and a 3 ton split system from them back in 2013. Both Goodman. Systems have been running well since. Had one control board die. I put a 24VAC surge and spike protector on it.
That chinese R22 has to be a scam. I'll bet you will never get your product. IMO, I think you should go all 410a while you can. |
|
|
[#42]
|
|
"The credit belongs to the man who is actually in the boogaloo, whose face is marred by pixels and ink and cheetos.”,
Teddy the Toad, (w,stte), "The Derpmen" |
[#43]
I have a fussy bearing in a Carrier condenser fan motor. The unit is almost 17 years old. R-410A. Repair or replace?
|
|
|
[Last Edit: SWIRE]
[#44]
Is there any type of unit sizing adjustment factor when it comes to R value of the walls, single pane windows, and little/no insulation? I have an old house with solid brick walls which means no insultation. The R value of my walls is around 1.5. I also have single pane wood windows, half don't have storm windows any more. Plus I have 10 ft ceilings with negligible insulation above them.
I'm curious compared to say a 1980s new build what the heating/cooling factor would be. Once the house reaches the set temp is something like 20% extra to maintain it or is air/heat basically just blowing away and it would be 200% more to maintain the temp? Is there any general like such as given a wall value of R-13 for every point lower increase the capacity requirement by X? Let's say 2% for each point, R-13 down to R-2 would be 11 points or 22%. Then instead of a 3 ton unit I know I need a 3.5 ton unit. Any general rule like that exist? |
|
Get Active or Get Disarmed! That means get involved in helping good candidates in primary and general election. That is in addition to being politically active once they are elected.
|
[#45]
Originally Posted By SWIRE: Is there any type of unit sizing adjustment factor when it comes to R value of the walls, single pane windows, and little/no insulation? I have an old house with solid brick walls which means no insultation. The R value of my walls is around 1.5. I also have single pane wood windows, half don't have storm windows any more. Plus I have 10 ft ceilings with negligible insulation above them. I'm curious compared to say a 1980s new build what the heating/cooling factor would be. Once the house reaches the set temp is something like 20% extra to maintain it or is air/heat basically just blowing away and it would be 200% more to maintain the temp? Is there any general like such as given a wall value of R-13 for every point lower increase the capacity requirement by X? Let's say 2% for each point, R-13 down to R-2 would be 11 points or 22%. Then instead of a 3 ton unit I know I need a 3.5 ton unit. Any general rule like that exist? View Quote No such formula exists that I am aware of. Each house needs a custom manual J to determine these factors. |
|
What is a democrat? Someone who wants everything you have, except for your job.
Politicians should wear uniforms like NASCAR drivers so we could see their corporate sponsors. |
[#46]
Originally Posted By ZW17: No such formula exists that I am aware of. Each house needs a custom manual J to determine these factors. View Quote View All Quotes View All Quotes Originally Posted By ZW17: Originally Posted By SWIRE: Is there any type of unit sizing adjustment factor when it comes to R value of the walls, single pane windows, and little/no insulation? I have an old house with solid brick walls which means no insultation. The R value of my walls is around 1.5. I also have single pane wood windows, half don't have storm windows any more. Plus I have 10 ft ceilings with negligible insulation above them. I'm curious compared to say a 1980s new build what the heating/cooling factor would be. Once the house reaches the set temp is something like 20% extra to maintain it or is air/heat basically just blowing away and it would be 200% more to maintain the temp? Is there any general like such as given a wall value of R-13 for every point lower increase the capacity requirement by X? Let's say 2% for each point, R-13 down to R-2 would be 11 points or 22%. Then instead of a 3 ton unit I know I need a 3.5 ton unit. Any general rule like that exist? No such formula exists that I am aware of. Each house needs a custom manual J to determine these factors. If I am not mistaken, a manual J will take into account different wall constructions / insulation levels and the same for windows / fenestration losses. (to Swire's concern) |
|
|
Sign up for the ARFCOM weekly newsletter and be entered to win a free ARFCOM membership. One new winner* is announced every week!
You will receive an email every Friday morning featuring the latest chatter from the hottest topics, breaking news surrounding legislation, as well as exclusive deals only available to ARFCOM email subscribers.
AR15.COM is the world's largest firearm community and is a gathering place for firearm enthusiasts of all types.
From hunters and military members, to competition shooters and general firearm enthusiasts, we welcome anyone who values and respects the way of the firearm.
Subscribe to our monthly Newsletter to receive firearm news, product discounts from your favorite Industry Partners, and more.
Copyright © 1996-2024 AR15.COM LLC. All Rights Reserved.
Any use of this content without express written consent is prohibited.
AR15.Com reserves the right to overwrite or replace any affiliate, commercial, or monetizable links, posted by users, with our own.