Posted: 7/24/2024 8:25:08 PM EDT
I'm trying to figure out what it would take to run 50amp @ 240vac for 300feet, but the calculators I'm finding online don't seem to like these numbers. Can anyone tell me what it would take?
Link Posted: 7/24/2024 8:43:56 PM EDT
[#1]
OST. I tried to do this many years ago but the answers gave me "2 gauge wire'' or some such.
Link Posted: 7/24/2024 8:56:59 PM EDT
[#2]
Link Posted: 7/24/2024 8:57:18 PM EDT
[Last Edit: voodoocustomz] [#3]
I come up with #3 copper, or 1/0 aluminum.

ETA

1 conductor per phase utilizing a 3 AWG copper conductor installed Cable, Conduit (non-Steel), & Direct Burial will limit the voltage drop to 2.93% or less when supplying 50 amps for 300 feet on a 240 volt single phase system.


Engineering Information

85Amps Rated ampacity of selected conductor
0.2379Ohms Resistance (Ohms per 1000 feet)
0.0470Ohms Reactance (Ohms per 1000 feet)
0.9Power Factor
7.20Maximum allowable voltage drop at 3%
7.038Actual voltage drop loss at 2.93% for the circuit
Link Posted: 7/24/2024 9:59:29 PM EDT
[#4]
Pretty good haul for 50a. What exactly is the load?  Motor, sub panel?
Link Posted: 7/24/2024 10:30:43 PM EDT
[#5]
Discussion ForumsJump to Quoted PostQuote History
Originally Posted By DVCER:
Pretty good haul for 50a. What exactly is the load?  Motor, sub panel?
View Quote

Sub panel. Two RVs, an air conditioner,  and lights.
Link Posted: 7/25/2024 2:45:07 PM EDT
[#6]
Discussion ForumsJump to Quoted PostQuote History
Originally Posted By voodoocustomz:
I come up with #3 copper, or 1/0 aluminum.

ETA

1 conductor per phase utilizing a 3 AWG copper conductor installed Cable, Conduit (non-Steel), & Direct Burial will limit the voltage drop to 2.93% or less when supplying 50 amps for 300 feet on a 240 volt single phase system.


Engineering Information

85Amps Rated ampacity of selected conductor
0.2379Ohms Resistance (Ohms per 1000 feet)
0.0470Ohms Reactance (Ohms per 1000 feet)
0.9Power Factor
7.20Maximum allowable voltage drop at 3%
7.038Actual voltage drop loss at 2.93% for the circuit
View Quote

Great info. And then I'd want the same size for the neutral since I'll be drawing rather high current on 120volt. How do I size the ground?
Link Posted: 7/25/2024 7:02:30 PM EDT
[Last Edit: zeekh] [#7]
Discussion ForumsJump to Quoted PostQuote History
Originally Posted By Imzadi:

Great info. And then I'd want the same size for the neutral since I'll be drawing rather high current on 120volt. How do I size the ground?
View Quote



Not an electrician, AFAIK, ground can be 2 sizes smaller than feed wires.
Link Posted: 7/29/2024 7:16:47 PM EDT
[#8]
Discussion ForumsJump to Quoted PostQuote History
Originally Posted By Imzadi:

Great info. And then I'd want the same size for the neutral since I'll be drawing rather high current on 120volt. How do I size the ground?
View Quote

You just want a quadplex wire which will come with a smaller ground.

It might be cheaper to get another pole and service installed.
Link Posted: 7/30/2024 2:15:22 PM EDT
[#9]
Discussion ForumsJump to Quoted PostQuote History
Originally Posted By zeekh:



Not an electrician, AFAIK, ground can be 2 sizes smaller than feed wires.
View Quote


You’re thinking neutral/grounded conductor.

Op, your ground is based going to be based on the size of breaker protecting the circuit. It doesn’t have to be resized for voltage drop like grounded conductors. For a 50a circuit it’s 10ga copper for ground.
Link Posted: 7/30/2024 2:19:19 PM EDT
[#10]
Discussion ForumsJump to Quoted PostQuote History
Originally Posted By Imzadi:

Sub panel. Two RVs, an air conditioner,  and lights.
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Originally Posted By Imzadi:
Originally Posted By DVCER:
Pretty good haul for 50a. What exactly is the load?  Motor, sub panel?

Sub panel. Two RVs, an air conditioner,  and lights.


You are going to power TWO RV's, and another A/C unit, on 50 amps?
Link Posted: 7/30/2024 2:31:59 PM EDT
[#11]
I always thought the most affordable is mobile home service entrance wire, like 2-2-2-4 AL.  

https://www.lowes.com/pd/Southwire-2-2-2-4-Black-Stranded-Al-MHF-Use-2-Cable/5002300757

I don't think 2 is big enough tho.

https://paigeconnected.com/calculators/wiresize-calculator
https://www.southwire.com/calculator-vdrop
Link Posted: 7/30/2024 2:37:13 PM EDT
[Last Edit: diamondd817] [#12]
6 gauge, or 4 gauge if you really want to overcompensate.

4/3 with ground.
Link Posted: 7/30/2024 2:43:36 PM EDT
[#13]
Discussion ForumsJump to Quoted PostQuote History
Originally Posted By diamondd817:
6 gauge, or 4 gauge if you really want to overcompensate.

4/3 with ground.
View Quote

What constitutes an acceptable voltage drop to you?
Link Posted: 7/31/2024 5:27:45 PM EDT
[#14]
Discussion ForumsJump to Quoted PostQuote History
Originally Posted By lethe:


You’re thinking neutral/grounded conductor.

Op, your ground is based going to be based on the size of breaker protecting the circuit. It doesn’t have to be resized for voltage drop like grounded conductors. For a 50a circuit it’s 10ga copper for ground.
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Originally Posted By lethe:
Originally Posted By zeekh:



Not an electrician, AFAIK, ground can be 2 sizes smaller than feed wires.


You’re thinking neutral/grounded conductor.

Op, your ground is based going to be based on the size of breaker protecting the circuit. It doesn’t have to be resized for voltage drop like grounded conductors. For a 50a circuit it’s 10ga copper for ground.



Separate neutral and grounds in a sub panel. Ground back to main panel can be 2 sizes smaller.  Neutral same size as hot wires.
Link Posted: 7/31/2024 7:09:37 PM EDT
[#15]
Discussion ForumsJump to Quoted PostQuote History
Originally Posted By zeekh:



Separate neutral and grounds in a sub panel. Ground back to main panel can be 2 sizes smaller.  Neutral same size as hot wires.
View Quote


Where are you getting that a ground can be 2 sizes smaller. It’s based on your ocpd size, not the size of your “hot” wires.
Link Posted: 7/31/2024 7:35:06 PM EDT
[#16]
Discussion ForumsJump to Quoted PostQuote History
Originally Posted By lethe:


Where are you getting that a ground can be 2 sizes smaller. It’s based on your ocpd size, not the size of your “hot” wires.
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Originally Posted By lethe:
Originally Posted By zeekh:



Separate neutral and grounds in a sub panel. Ground back to main panel can be 2 sizes smaller.  Neutral same size as hot wires.


Where are you getting that a ground can be 2 sizes smaller. It’s based on your ocpd size, not the size of your “hot” wires.



Unsure what ocpd size is.

I used #2 copper wire for 2 hots and a neutral from main panel to sub panel. #4 copper wire for ground from main panel  to sub panel. Had my subpage inspected, it passed. Also had have ground rod at the sub panel.
Link Posted: 7/31/2024 7:48:13 PM EDT
[#17]
Discussion ForumsJump to Quoted PostQuote History
Originally Posted By zeekh:



Unsure what ocpd size is.

I used #2 copper wire for 2 hots and a neutral from main panel to sub panel. #4 copper wire for ground from main panel  to sub panel. Had my subpage inspected, it passed. Also had have ground rod at the sub panel.
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Originally Posted By zeekh:
Originally Posted By lethe:
Originally Posted By zeekh:



Separate neutral and grounds in a sub panel. Ground back to main panel can be 2 sizes smaller.  Neutral same size as hot wires.


Where are you getting that a ground can be 2 sizes smaller. It’s based on your ocpd size, not the size of your “hot” wires.



Unsure what ocpd size is.

I used #2 copper wire for 2 hots and a neutral from main panel to sub panel. #4 copper wire for ground from main panel  to sub panel. Had my subpage inspected, it passed. Also had have ground rod at the sub panel.


OCPD = overcurrent protection device.  The amperage rating of the breaker for the sub panel, will determine the minimum grounding conductor wire size.
Link Posted: 7/31/2024 7:52:17 PM EDT
[#18]
Discussion ForumsJump to Quoted PostQuote History
Originally Posted By FALARAK:

What constitutes an acceptable voltage drop to you?
View Quote


In the real world, 1,000 ft or more.
Link Posted: 7/31/2024 8:02:40 PM EDT
[#19]
Discussion ForumsJump to Quoted PostQuote History
Originally Posted By diamondd817:


In the real world, 1,000 ft or more.
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Originally Posted By diamondd817:
Originally Posted By FALARAK:

What constitutes an acceptable voltage drop to you?


In the real world, 1,000 ft or more.


5%
Link Posted: 7/31/2024 10:06:34 PM EDT
[#20]
Discussion ForumsJump to Quoted PostQuote History
Originally Posted By zeekh:



Unsure what ocpd size is.

I used #2 copper wire for 2 hots and a neutral from main panel to sub panel. #4 copper wire for ground from main panel  to sub panel. Had my subpage inspected, it passed. Also had have ground rod at the sub panel.
View Quote


You way oversized your ground. Nothing wrong with it being oversized but saying you can go two sizes smaller than the ungrounded conductors (hot) is going to get someone to fail an inspection.

In some cases grounded conductors (neutrals) can be sized two sizes smaller than ungrounded conductors but that’s not the case at all for the grounding conductor.
Link Posted: 8/1/2024 5:12:21 AM EDT
[#21]
Discussion ForumsJump to Quoted PostQuote History
Originally Posted By lethe:


Where are you getting that a ground can be 2 sizes smaller. It’s based on your ocpd size, not the size of your “hot” wires.
View Quote View All Quotes
View All Quotes
Discussion ForumsJump to Quoted PostQuote History
Originally Posted By lethe:
Originally Posted By zeekh:



Separate neutral and grounds in a sub panel. Ground back to main panel can be 2 sizes smaller.  Neutral same size as hot wires.


Where are you getting that a ground can be 2 sizes smaller. It’s based on your ocpd size, not the size of your “hot” wires.



Your ocpd is based on ampacity of your wire correct?

Link Posted: 8/1/2024 6:42:13 AM EDT
[#22]
Discussion ForumsJump to Quoted PostQuote History
Originally Posted By lethe:


You’re thinking neutral/grounded conductor.

Op, your ground is based going to be based on the size of breaker protecting the circuit. It doesn’t have to be resized for voltage drop like grounded conductors. For a 50a circuit it’s 10ga copper for ground.
View Quote



250.122(B) would disagree.
Link Posted: 8/7/2024 9:44:26 PM EDT
[#23]
300' I would run #4 copper
Link Posted: 8/9/2024 7:46:02 PM EDT
[#24]
Discussion ForumsJump to Quoted PostQuote History
Originally Posted By zeekh:



Separate neutral and grounds in a sub panel. Ground back to main panel can be 2 sizes smaller.  Neutral same size as hot wires.
View Quote



HUGE.     Neutral and ground MUST be separate on a sub panel.  They can only be bonded at the main unless you want problems.