9/23/2017 7:46:55 PM EDT
This was inspired by this thread:  https://www.ar15.com/forums/general/Someone-school-me-on-backfeeding-or-pig-tailing-a-generator-back-into-the-house-/5-2032540/

If you can make it through all the ridiculous pages of purse swinging.... there was some good info in there, and it got me off my butt to do this.  Thanks to the contributors there.

I have a Champion 3100W Gas/Propane generator that I bought specifically just to have just in case.  Power outages are not typical in Dallas, Texas.

I have a Square D QO style breaker panel, and wanted to do a safe panel feed.  Here is what I bought:

$51 - Inlet box 30 amp - http://a.co/dL7xPtE
$51 - Interlock for SquareD QO panel - http://a.co/dC0yn0g
$27 - Wire for breaker to inlet box - http://www.homedepot.com/p/Southwire-15-ft-10-3-Solid-Romex-SIMpull-CU-NM-B-W-G-Wire-63948427/202525532
$16 - 30 amp Breaker for backfeed - http://www.homedepot.com/p/Square-D-QO-30-Amp-Two-Pole-Circuit-Breaker-QO230CP/100022140
-------------------------------------
$145

This is all you need for the base install.

Then - you need a cord for your generator, and optionally an adapter for the inlet box to your cord type.  My generator has RV 120v 30 amp output, so I chose an RV cord and an adapter that bridges the two hots on the inlet together to power both sides of my panel:

$40 - 50 foot RV extension cord - http://a.co/8eRehRj
$45 - RV to L-1430R bridged adapter - http://a.co/0awn1BK
-------------------------------------
$85



Before:



The stuff:




I needed to move some circuits around to get room for this position and a 220v breaker.  Luckily I found out in that thread QO breakers allow two conductors per breaker, so that made life easy for me.




Installed the 30amp 220v backfeed breaker:




Then wired it up.  Using 10/3 wire and pulling to my location for the generator inlet.













Next, on the interlock kit, you install a bracket to warn people about this "special breaker" if the panel is open:





Drill some holes using the provided template with the interlock kit:




Then install the interlock with the provided screws:




Hooked up:




House is running on gen power, with both sides of the panel hot with 120v, using the bridge in the adapter above.




I have a milk crate to store the cord and all the generator accessories, so its all ready to go in one place:

9/23/2017 7:50:25 PM EDT
[#1]
That's awesome man.
9/23/2017 7:52:50 PM EDT
[#2]
THIS is what happens where there aren't any good hookers in your town.  
9/23/2017 7:53:06 PM EDT
[#3]
You could have used this dedicated transfer switch for less money.

Generac
9/23/2017 7:53:22 PM EDT
[#4]
9/23/2017 7:55:39 PM EDT
[#5]
Quote History
Quoted:
You could have used this dedicated transfer switch for less money.

Generac
View Quote
Not really.

That transfer switch handles 6 circuits (as sold) for $226.

You need to supply a 60 amp breaker from your main box to feed this.
You still need a cord, and a bridged adapter to feed a 120v only generator (like mine) into this panel.

So a correct comparison would be:

My solution:  Interlock, Inlet box, wire, breaker = $145.

versus yours:  Generac transfer switch + 60 amp breaker = $248.  If you want your inlet box outside the house, you have to buy that seperate, so another $51 (inlet) + $27 (wire) added to that, making your recommendation $326.

Transfer switch has 6 circuits (could be 10 with added costs) yet my breaker panel has 26 120v circuits that I can pick and choose from.


@DamascusKnifemaker - Doing your recommendation would cost more than twice as much.
9/23/2017 7:55:54 PM EDT
[#6]
Did I make it in before the people afraid of electrical work or the electricians that can't handle homeowners doing their own work?

Nice job OP. I have very similar setup.
9/23/2017 7:57:49 PM EDT
[#7]
ost
9/23/2017 8:00:19 PM EDT
[#8]
Quote History
Quoted:
ost
View Quote
9/23/2017 8:02:10 PM EDT
[#9]
Good job OP.
9/23/2017 8:10:00 PM EDT
[#10]
I know I should do that. But I have some anxiety about it.

Thank you very much for this post...
9/23/2017 8:31:37 PM EDT
[#11]
Looks good.

Is there a similar setup for 220?
9/23/2017 8:37:02 PM EDT
[#12]
Nice job op. I hope to do the same for my house eventually.
9/23/2017 8:44:20 PM EDT
[#13]
Quote History
Quoted:

Looks good.

Is there a similar setup for 220?
View Quote
This is a 240V setup.

I dont have a 240V generator, so I use the adapter to bridge the two hot legs, which provides 110 to both legs of the panel, and I keep my 240v breakers off.

If I had a 240V generator, all I'd need is a cord, hook it up, and done.  However, if I was going to go 240V route, I'd use a bigger generator, and use the 50amp inlet, breaker, and properly sized wire.
9/23/2017 8:52:00 PM EDT
[#14]
That energized, exposed, blade on your pigtail concerns me.
9/23/2017 8:53:31 PM EDT
[#15]
Tag, because I need to do this.
9/23/2017 8:57:56 PM EDT
[#16]
Quote History
Quoted:
That energized, exposed, blade on your pigtail concerns me.
View Quote
@sparky923 - Explain how that is energized?
9/23/2017 8:59:51 PM EDT
[#17]
Looks good! Mine is very similar also but I did go with 220V. Got a 8KW generator on propane and it's been nice. Just to be able to flush the head was worth the $$.

I do like the milk carton idea. I need to copy that.
9/23/2017 9:00:43 PM EDT
[#18]
Quote History
Quoted:
That energized, exposed, blade on your pigtail concerns me.
View Quote
What are you looking at.  I'm missing it.  Blade?
9/23/2017 9:03:19 PM EDT
[#19]
9/23/2017 9:03:54 PM EDT
[#20]
Quote History
Quoted:
What are you looking at.  I'm missing it.  Blade?
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
That energized, exposed, blade on your pigtail concerns me.
What are you looking at.  I'm missing it.  Blade?
I am missing it also.
9/23/2017 9:04:05 PM EDT
[#21]
Quote History
Quoted:


What are you looking at.  I'm missing it.  Blade?
View Quote
And it's not at 45 degrees. Hideous.
9/23/2017 9:04:29 PM EDT
[#22]
You're gonna burn your house down.
9/23/2017 9:07:43 PM EDT
[#23]
Okay i guess

You spent all that money to hook up.a 2k watt genny.

You would have been just as good with decent cords
9/23/2017 9:09:47 PM EDT
[#24]
Quote History
Quoted:
You're gonna burn your house down.
View Quote
And put your eye out too.
9/23/2017 9:10:01 PM EDT
[#25]
Why all the dam plugs? Run the generator wire straight to the damn breaker in the panel, turn off the main, start the generator and let it eat.

All those damn plugs are a point of heat and voltage drop.
9/23/2017 9:18:09 PM EDT
[#26]
In before the you'll kill everyone on the block and lock 
tagging because I'm doing this at my new place 
9/23/2017 9:30:50 PM EDT
[#27]
Nice. Working on gathering my own parts as well. Having my electrician remove the tamper tag and meter to replace my main 2 x 6", 100amp breaker with a 2 x 3" without an issue to open some space for the inlet breaker is where I am.. Have the new inlet breaker, waiting on the 100a main breaker (Monday). Once I have that done I will order the inlet box, interlock, and accessories. No point in spending the money until you need to.

9/23/2017 11:05:46 PM EDT
[#28]
Quote History
Quoted:
I know I should do that. But I have some anxiety about it.

Thank you very much for this post...
View Quote
I just did my mechanical interlock today.


Installing mechanical interlock for portable generator for house
9/23/2017 11:15:28 PM EDT
[#29]
Nice OP. I'll be doing the same very soon.
9/23/2017 11:25:42 PM EDT
[#30]
Quote History
Quoted:
Did I make it in before the people afraid of electrical work or the electricians that can't handle homeowners doing their own work?

Nice job OP. I have very similar setup.
View Quote
Only thing I want to know is how do you cut power to the breaker/haus?
9/23/2017 11:25:57 PM EDT
[#31]
tagging this thread b/c it interests me.  I just grabbed a brand new in box 8k watt generator from my parents that are moving. They bought it but never ran it, and I would like a way to run it at my house.
9/23/2017 11:35:20 PM EDT
[#32]
Bought the whole Inlet box/transfer switch/cable kit for $100 from a guy on Craigslist that made a lot of repetitive movements..(arfcom later told me it was meth) ..Sold the 6 outlet transfer switch because I had a well and that took 2 outlets right there.  Paid $100 to a moonlighting electrician to hook up inlet box, power cable and $65 interlock ..paid something like $150 for 8.5 kw generator bought at  online auction.  Paid $95 for Motorsnorkel when they were offering arfcommers a deal ..

now I just have to figure out a way to run NG to the driveway
9/23/2017 11:36:01 PM EDT
[#33]
I've got 400A service with the two main breakers by the meter box and two panels (no mains) in the garage.

Transfer switch for me I guess.  
9/23/2017 11:38:36 PM EDT
[#34]
OST

This is something I've been very interested in.
9/23/2017 11:43:41 PM EDT
[#35]
Good work OP! That bridge adapter is a must have for people already wired for a normal 30 amp 240V inlet to the panel, makes having a second more efficient generator with a dedicated 30 amp 120V RV outlet a viable solution for longer run times when the big unit isn't needed.
9/23/2017 11:50:40 PM EDT
[#36]
Quote History
Quoted:

Only thing I want to know is how do you cut power to the breaker/haus?
View Quote
Turn off the main?  Work safely so you don't touch the two big wires going into the main breaker. Not really a big deal.

I have a 200 amp disconnect at my meter so I can kill the power before it gets to the main breaker on my 200 amp panel.  Makes working on my main panel very safe.
9/24/2017 12:02:50 AM EDT
[#37]
I’ve always wondered why more people don’t just use an external transfer switch to switch everything from utility to generator? A 100 amp manual transfer switch isn’t very expensive and then you’re done.

ETA: Not picking at you OP, your setup will work just fine and with the interlock you’re good. Just wondering.
9/24/2017 12:05:55 AM EDT
[#38]
Got a pic of the bridge wire inside the pigtail?

Edit : Nevermind, I see you bought an already bridged pigtail.
9/24/2017 12:15:16 AM EDT
[#39]
Quote History
Quoted:
Got a pic of the bridge wire inside the pigtail?

Edit : Nevermind, I see you bought an already bridged pigtail.
View Quote
If you want to make your own, the X & Y wire connections in the 240V Nema L14-30R end need to be connected to the 4 wire cable normally then both of them at the 120V TT-30 P 30 amp RV plug need to tag the single hot lug on the connector. W & G (white and green) get connected as they normally would between the two connector ends.
9/24/2017 1:06:54 AM EDT
[#40]
Quote History
Quoted:
I’ve always wondered why more people don’t just use an external transfer switch to switch everything from utility to generator? A 100 amp manual transfer switch isn’t very expensive and then you’re done.

ETA: Not picking at you OP, your setup will work just fine and with the interlock you’re good. Just wondering.
View Quote
Can't speak for others but in my case I'd have to pull the meter to do it safely.  Pulling the meter is a royal PITA involving paperwork with the utility and hiring an electrician.  So doing an interlock kit is actually a cost saver.

For the record I have a 200 Amp Automatic switch in the attic.  The cost issue aside, I'd have to install it next to the breaker box outside of my fence which is not ideal.  So any kid could mess with it.  Then I'd have to run a cord around the house if I wanted to keep the gens in the backyard.

Point being it could be any number of reasons to do this. Cost being part of it or logistics.
9/24/2017 10:40:31 AM EDT
[#41]
https://www.ar15.com/forums/outdoors/Back_feeding_your_panel_using_an_interlock__project_AAR_w__pics/17-651376/

My thread on the same topic.  You'll need the chrome add on to see the photobucket pics.

Nice work, op
9/24/2017 11:20:27 AM EDT
[#42]


9/24/2017 11:51:05 AM EDT
[#43]
Why do people not use the  QO2DTI for the QO panels?

https://www.amazon.com/gp/offer-listing/B00PSMTCWW/ref=dp_olp_new_mbc?ie=UTF8&condition=new

No fuss, no muss and it's rated by the manufacturer, used in some of their panels and is at least $30.00 less expensive than the one in this thread when purchased at an electrical store.

The following is the manufacturer's video:

https://www.youtube.com/watch?v=TSV0sFWYLME

Good job OP!
9/24/2017 11:52:48 AM EDT
[#44]
Very nive job!
9/24/2017 11:59:20 AM EDT
[#45]
Quote History
Quoted:
This is a 220V setup.

I dont have a 220V generator, so I use the adapter to bridge the two hot legs, which provides 110 to both legs of the panel, and I keep my 220v breakers off.

If I had a 220V generator, all I'd need is a cord, hook it up, and done.  However, if I was going to go 220V route, I'd use a bigger generator, and use the 50amp inlet, breaker, and properly sized wire.
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:

Looks good.

Is there a similar setup for 220?
This is a 220V setup.

I dont have a 220V generator, so I use the adapter to bridge the two hot legs, which provides 110 to both legs of the panel, and I keep my 220v breakers off.

If I had a 220V generator, all I'd need is a cord, hook it up, and done.  However, if I was going to go 220V route, I'd use a bigger generator, and use the 50amp inlet, breaker, and properly sized wire.
That was my first concern but you addressed it...





...and it's 240v, not 220v
9/24/2017 12:31:05 PM EDT
[#46]
Quote History
Quoted:


@sparky923 - Explain how that is energized?
View Quote
Sorry, I see a cord plugged in to the wall backwards, and I don't consider at first that it won't be energized because of the interlock. You're good, I'm used to finding installs where there wouldn't be an interlock and a homeowner wouldn't think twice about a live panel energizing that cord cap.
9/24/2017 12:38:50 PM EDT
[#47]
My interlock. It was very inexpensive at Ace Hardware.


9/24/2017 12:43:15 PM EDT
[#48]
How loud is a propane-powered generator compared to a gasoline powered generator?
9/24/2017 12:43:30 PM EDT
[#49]
NICELY DONE!
9/24/2017 1:11:53 PM EDT
[#50]
Quote History
Quoted:
Why do people not use the  QO2DTI for the QO panels?

https://www.amazon.com/gp/offer-listing/B00PSMTCWW/ref=dp_olp_new_mbc?ie=UTF8&condition=new

No fuss, no muss and it's rated by the manufacturer, used in some of their panels and is at least $30.00 less expensive than the one in this thread when purchased at an electrical store.

The following is the manufacturer's video:

https://www.youtube.com/watch?v=TSV0sFWYLME

Good job OP!
View Quote
In the OP's panel, that particular interlock would not work.
His main breaker is a couple inches above his gen. back feed breaker.

Great job OP!