5/9/2015 5:50:12 PM EDT
The condenser was making a strange sound, I went out to check on it and the unit was hot and the fan was not running, only the compressor was running, the backside of the motor where it mounts felt hot, even though it was not spinning/running.

I only have a simple multimeter, so I can not check the capacitor, but it does not look "bulged".

Is it safe to say that all I need is a new fan motor, or is it something else? I was going to order a fan motor, but now I'm not sure if that is the problem, since I can't check the capacitor.

Should I order a fan motor and a capacitor and be good to go, or is there something else that it could be?

I don't want to waste my time with the motor and the capacitor if that is not the issue.
5/9/2015 5:51:28 PM EDT
[#1]
try turning the blade with a screwdriver to get it started.

Probably just needs a motor.
5/9/2015 5:52:46 PM EDT
[#2]
Age and make ?
5/9/2015 5:52:58 PM EDT
[#3]
The starter capacitor will usually fail with no visible signs.  Replace that first before thinking about replacing the motor.


5/9/2015 5:53:43 PM EDT
[#4]
Mine was a fan motor failure when I had a similar experience.
5/9/2015 5:56:09 PM EDT
[#5]

Quote History
Quoted:


Age and make ?
View Quote
14 year old unit

Goodman

model: CPKJ36-1AB



 
5/9/2015 5:56:47 PM EDT
[#6]
If you are going to do your own DIY work, this would be a good time to invest in a digital multimeter.
5/9/2015 6:06:02 PM EDT
[#7]
Power Off


U can check the cap with a standard ohmmeter. First discharge the cap with a screwdriver. With the meter on ohms check the cap, then pull the leads and reverse them on the cap. If you get a bump on the meter it pretty much tells you it good. This is crude way but it works most of the time.
5/9/2015 6:21:07 PM EDT
[#8]




Here is a picture of my capacitor, part number is: P/N: B94575500
" />
I found this on Amazon but it isn't prime:




CAPACITOR 40+5 MFD 370 VAC ROUND ONETRIP PARTS® DIRECT REPLACEMENT FOR AMANA GOODMAN JANITROL OEM PART CAP050400370R












  • 40+5 MFD - 370 VAC




  • 2" Round Base Dimension




  • Used on Amana, Goodman, and Janitrol Units













I found this capacitor on amazon Prime and would like to order it :




Packard TRCFD355 35+5 MFD 440/370V ROUND Capacitor









       







  • Round dual run capacitor 35 + 5 MFD 370V and 440V.  Can size measures 1.97" diameter x 4.13" tall.




  • Heavy-edged metalized polypropylene film is used for the
    dielectric. Proprietary bio-degradable oil. Second generation
    anti-explosion safety switch.




  • Built to the toughest international standards for AC motor
    run capacitors including EIA-456-A and IEC 60252-1:2001. 100%
    electrical tested.




  • Typically found in air conditioner units.




  • Replaces either a 370V or 440V 30/5MFD round dual run cap.





     


 
 
5/9/2015 6:23:48 PM EDT
[#9]
Is there a C F and H on top of the cap?
5/9/2015 6:28:49 PM EDT
[#10]
That is a common capacitor, any HVAC parts store should be able to sell you a replacement for $5 ~ $10.  Take a picture of the top connections, remove and take it with you to get a replacement.  

If they have different grades (prices) get the more expensive part.  The last couple of Chinese caps I put in my HVAC only lasted a couple of years before dying.

5/9/2015 6:29:03 PM EDT
[#11]
14 years old? I would replace both the cap and the fan.
5/9/2015 7:25:15 PM EDT
[#12]
Quote History
Quoted:
14 year old unit
Goodman
model: CPKJ36-1AB
 
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
Age and make ?
14 year old unit
Goodman
model: CPKJ36-1AB
 



Get est..ffor new unit. At this  age u are throwing good $$ after bad.

Get a 16 SEER, cut your bill by 25 % and be hapPy. Invest savings into new duct work
5/9/2015 7:28:49 PM EDT
[#13]
Quote History
Quoted:



Get est..ffor new unit. At this  age u are throwing good $$ after bad.

Get a 16 SEER, cut your bill by 25 % and be hapPy. Invest savings into new duct work
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
Quoted:
Age and make ?
14 year old unit
Goodman
model: CPKJ36-1AB
 



Get est..ffor new unit. At this  age u are throwing good $$ after bad.

Get a 16 SEER, cut your bill by 25 % and be hapPy. Invest savings into new duct work

You must be in the sales department.
5/9/2015 7:30:49 PM EDT
[#14]
Unless you can't turn the fan blade by hand or the whole shaft wobbles like crazy, replace the capacitor first.  You probably don't need a new fan motor.
5/9/2015 7:35:21 PM EDT
[#15]
Capacitor first then the motor.
5/9/2015 7:49:09 PM EDT
[#16]
Could be the cap or could be the motor.
5/9/2015 7:59:39 PM EDT
[#17]
100% sure it's the contactor switch, if the contacts are pitted and black, thats your problem.

For a temp fix you can shut the power off then sand or file the contacts and it will usually work for a short period. If you have an unused side of contacts, just switch the wires over and send me $100.00.
5/9/2015 8:18:52 PM EDT
[#18]
Quote History
Quoted:
100% sure it's the contactor switch, if the contacts are pitted and black, thats your problem.

For a temp fix you can shut the power off then sand or file the contacts and it will usually work for a short period. If you have an unused side of contacts, just switch the wires over and send me $100.00.
View Quote

Most small condenser units run the fan and compressor off the same contactor.

OP's compressor is running. (or at least trying to). The contactor is probably fine.
5/9/2015 8:35:35 PM EDT
[#19]
Contactor is fine, it engages.
5/9/2015 8:39:57 PM EDT
[#20]
What's your amp draw on the fan motor?
5/9/2015 8:44:42 PM EDT
[#21]

Quote History
Quoted:


What's your amp draw on the fan motor?
View Quote
Is that listed on the motor, or do I need a clamp on amp meter?

 
5/9/2015 8:53:39 PM EDT
[#22]
Quote History
Quoted:
Contactor is fine, it engages.
View Quote
Engages means nothing, can still be the problem even if contact is made.
5/9/2015 8:58:16 PM EDT
[#23]

Quote History
Quoted:



Engages means nothing, can still be the problem even if contact is made.

View Quote View All Quotes
View All Quotes
Quote History
Quoted:



Quoted:

Contactor is fine, it engages.
Engages means nothing, can still be the problem even if contact is made.

I have 220 coming out the other side, when I take a reading.

 
5/9/2015 8:58:32 PM EDT
[#24]
Quote History
Quoted:
Is that listed on the motor, or do I need a clamp on amp meter?  
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
What's your amp draw on the fan motor?
Is that listed on the motor, or do I need a clamp on amp meter?  

If you wanted to check it, you'd have to have an amp clamp and compare the reading versus what is listed on the motor plate.

Honestly you could probably figure this all out with just doing resistance checks with the power off. (and all wires disconnected)

Run cap - infinite resistance or shorted  = bad capacitor (you have to hold the ohmmeter leads on the capacitor terminals for several seconds to be sure)
Fan windings shorted to ground or a dead short to each other (2 ohm or less usually - but with some motors this is a normal resistance) ; or windings with infinite resistance to each other = bad fan motor.
5/9/2015 9:16:25 PM EDT
[#25]
I have the motor pulled out. Which wires do I check?
I have a brown wire, that went to the capacitor,

A blk wire, that went to the the contactor

And the purple wire, that went to the DF2 on the board.






5/9/2015 9:23:36 PM EDT
[#26]
Oh boy, this is about to get good.
5/9/2015 9:36:29 PM EDT
[#27]
Monday take the motor and capacitor to local HVAC parts house and buy replacements. Probably a generic replacement since it is a Goodman and probably less than $150 for both.
5/9/2015 9:42:45 PM EDT
[#28]
No local place, that sells to the public.
I'm stuck with Amazon or any other online retailer.
5/9/2015 9:44:23 PM EDT
[#29]
Quote History
Quoted:
14 year old unit
Goodman
model: CPKJ36-1AB
 
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
Age and make ?
14 year old unit
Goodman
model: CPKJ36-1AB
 

Its not worth fixing. Buy a new energy efficient model and it will pay for itself in no time.

Yes im a contractor.
5/9/2015 9:45:17 PM EDT
[#30]
Quote History
Quoted:
No local place, that sells to the public.I'm stuck with Amazon or any other online retailer.
View Quote


Washer specialties in ks is one of the cheapest online places.

They have been selling mail order hvac parts since you were knee high to a grasshopper.
5/9/2015 9:48:38 PM EDT
[#31]
Quote History
Quoted:



Get est..ffor new unit. At this  age u are throwing good $$ after bad.

Get a 16 SEER, cut your bill by 25 % and be hapPy. Invest savings into new duct work
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
Quoted:
Age and make ?
14 year old unit
Goodman
model: CPKJ36-1AB
 



Get est..ffor new unit. At this  age u are throwing good $$ after bad.

Get a 16 SEER, cut your bill by 25 % and be hapPy. Invest savings into new duct work


Awesome idea! Why spend $200 when you can blow a few grand on needless upgrades
5/9/2015 9:50:55 PM EDT
[#32]
Quote History
Quoted:


Awesome idea! Why spend $200 when you can blow a few grand on needless upgrades
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
Quoted:
Quoted:
Age and make ?
14 year old unit
Goodman
model: CPKJ36-1AB
 



Get est..ffor new unit. At this  age u are throwing good $$ after bad.

Get a 16 SEER, cut your bill by 25 % and be hapPy. Invest savings into new duct work


Awesome idea! Why spend $200 when you can blow a few grand on needless upgrades


Crunch the numbers. Some places it wont pay but if your electric bill is high it may actually be a savings.
5/9/2015 10:06:24 PM EDT
[#33]
Quote History
Quoted:
I have the motor pulled out. Which wires do I check?I have a brown wire, that went to the capacitor,
A blk wire, that went to the the contactor
And the purple wire, that went to the DF2 on the board.

View Quote

So you've got a heat pump then?

Check the fan motor resistance from Purple to Black, and Brown to Black (and then each to ground).

One thing that I am wondering, when everything is wired back up and powered on....do you lose voltage between contacts DF1 and DF2? If so, I think that would mean your unit thinks it's in defrost mode.

I wouldn't make any impulsive buys or repairs until you get a knowledgeable guy to take a look at it.
5/9/2015 10:13:10 PM EDT
[#34]

Quote History
Quoted:





So you've got a heat pump then?



Check the fan motor resistance from Purple to Black, and Brown to Black (and then each to ground).



One thing that I am wondering, when everything is wired back up and powered on....do you lose voltage between contacts DF1 and DF2? If so, I think that would mean your unit thinks it's in defrost mode.



I wouldn't make any impulsive buys or repairs until you get a knowledgeable guy to take a look at it.
View Quote View All Quotes
View All Quotes
Quote History
Quoted:



Quoted:

I have the motor pulled out. Which wires do I check?I have a brown wire, that went to the capacitor,

A blk wire, that went to the the contactor

And the purple wire, that went to the DF2 on the board.





So you've got a heat pump then?



Check the fan motor resistance from Purple to Black, and Brown to Black (and then each to ground).



One thing that I am wondering, when everything is wired back up and powered on....do you lose voltage between contacts DF1 and DF2? If so, I think that would mean your unit thinks it's in defrost mode.



I wouldn't make any impulsive buys or repairs until you get a knowledgeable guy to take a look at it.
Prpl to blk is 49.6 (with selector at 200 on ohm switch)

 
Brn to blk is 53.9
5/9/2015 10:17:35 PM EDT
[#35]
Earlier I checked the continuity on the board between DF1 and DF2 and it had continuity with DF1 wire removed.


5/9/2015 10:26:08 PM EDT
[#36]
They have a Grainger Industrial Supply in Asheville, Hickory, Gastonia, Greensboro, Fayetteville, Raleigh, Willmington, Greenville, Greensboro and Charlotte.  Any of them near you?  All should be walk in.  All should have that cap and probably a replacement motor.

Capacitor
5/9/2015 10:30:36 PM EDT
[#37]
Quote History
Quoted:
Prpl to blk is 49.6 (with selector at 200 on ohm switch)   Brn to blk is 53.9
View Quote

Resistance is a bit higher than I expected, but I doubt the motor is bad. Both windings are reading within 5 ohms of each other. Out of curiousity, are you using a good quality meter?
5/9/2015 10:31:15 PM EDT
[#38]
Quote History
Quoted:
Earlier I checked the continuity on the board between DF1 and DF2 and it had continuity with DF1 wire removed.

View Quote

That circuit is normally closed. (I looked at a generic Goodman heat pump wiring diagram). That means if the circuit board's relay energizes, it will break the connection between those two contacts. You have to do a voltage point-to-ground check at each terminal when the power is on and unit is running.
5/9/2015 10:33:17 PM EDT
[#39]
Quote History
Quoted:
100% sure it's the contactor switch, if the contacts are pitted and black, thats your problem.

For a temp fix you can shut the power off then sand or file the contacts and it will usually work for a short period. If you have an unused side of contacts, just switch the wires over and send me $100.00.
View Quote


If the contractor was bad nothing would be running. Most likely a bad fan motor. That capacitor is for the compressor.
5/9/2015 10:36:11 PM EDT
[#40]
Quote History
Quoted:

You must be in the sales department.
View Quote View All Quotes
View All Quotes
Quote History
Quoted:
Quoted:
Quoted:
Quoted:
Age and make ?
14 year old unit
Goodman
model: CPKJ36-1AB
 



Get est..ffor new unit. At this  age u are throwing good $$ after bad.

Get a 16 SEER, cut your bill by 25 % and be hapPy. Invest savings into new duct work

You must be in the sales department.


No shit, especially if it may only be a capacitor.
5/9/2015 10:39:27 PM EDT
[#41]
We have a Grainger, both my wife and I can use our employers accounts to shop there.
If I can figure out if the motor is bad before I get the new capacitor, I will bring the motor to them on Monday and see what they can order for me.

I have a capacitor coming from Amazon that will be here on Monday. I just don't want to drag this out any longer than I have to, it is supposed to be in the 80's next week.
5/9/2015 10:45:43 PM EDT
[#42]


Quote History
Quoted:
That circuit is normally closed. (I looked at a generic Goodman heat pump wiring diagram). That means if the circuit board's relay energizes, it will break the connection between those two contacts. You have to do a voltage point-to-ground check at each terminal when the power is on and unit is running.
View Quote View All Quotes
View All Quotes
Quote History
Quoted:





Quoted:


Earlier I checked the continuity on the board between DF1 and DF2 and it had continuity with DF1 wire removed.








That circuit is normally closed. (I looked at a generic Goodman heat pump wiring diagram). That means if the circuit board's relay energizes, it will break the connection between those two contacts. You have to do a voltage point-to-ground check at each terminal when the power is on and unit is running.
It's raining outside now and I don't want to put my pop up canopy up to work in the rain.

I have the motor inside the house.




 

Can I jump the wires from DF1 and DF2 tomorrow when I get a chance, will that tell me anything, should the motor come on?

 
5/9/2015 11:04:09 PM EDT
[#43]
Quote History
Quoted:
It's raining outside now and I don't want to put my pop up canopy up to work in the rain.I have the motor inside the house.
  Can I jump the wires from DF1 and DF2 tomorrow when I get a chance, will that tell me anything, should the motor come on?

 
View Quote

Just leave the motor out, and re-install the original wire back on DF1. Then, with the unit running, do a voltage point-to-ground check on both DF1 and DF2 and see if they are reading the same voltage.

You could also just carefully leave the wire off DF1 (the diagram I looked at showed the wire coming directly off the contactor - so it would be hot), and check continuity between DF1 and DF2 when the unit is running. If the circuit is open - then the defrost relay is engaged - and you are much further ahead in your troubleshooting then you were earlier this evening.
5/9/2015 11:11:17 PM EDT
[#44]

Quote History
Quoted:





Just leave the motor out, and re-install the original wire back on DF1. Then, with the unit running, do a voltage point-to-ground check on both DF1 and DF2 and see if they are reading the same voltage.



You could also just carefully leave the wire off DF1 (the diagram I looked at showed the wire coming directly off the contactor - so it would be hot), and check continuity between DF1 and DF2 when the unit is running. If the circuit is open - then you are much further ahead in your troubleshooting then you were earlier this evening.
View Quote View All Quotes
View All Quotes
Quote History
Quoted:



Quoted:

It's raining outside now and I don't want to put my pop up canopy up to work in the rain.I have the motor inside the house.

  Can I jump the wires from DF1 and DF2 tomorrow when I get a chance, will that tell me anything, should the motor come on?



 


Just leave the motor out, and re-install the original wire back on DF1. Then, with the unit running, do a voltage point-to-ground check on both DF1 and DF2 and see if they are reading the same voltage.



You could also just carefully leave the wire off DF1 (the diagram I looked at showed the wire coming directly off the contactor - so it would be hot), and check continuity between DF1 and DF2 when the unit is running. If the circuit is open - then you are much further ahead in your troubleshooting then you were earlier this evening.
Okay, I'll try that tomorrow and see what I get, thanks for the help .

 
5/11/2015 5:12:22 PM EDT
[#45]
Update- it was the capacitor.